 Snubber 
Author Message
Post Snubber
Hi all

I want to start a motor remotely.

The contactor coil is rated 240 volts and I am driving it with the
contacts of 12 volt DC relay driven by a microcontroller.

The relay contacts arc and I thought a snubber will reduce the arcing.
I checked various sites and ended up lots of calculations for which I
have no proper data.

Is there a ball park value I can use for the capacitor and the
resistor?

Thanks in advance for your time and attention

ClueLess

































--
Posted via a free Usenet account from http://www.teranews.com


17 Mar 2008, 17:08
Post Re: Snubber
ClueLess wrote:
> Hi all
>
> I want to start a motor remotely.
>
> The contactor coil is rated 240 volts and I am driving it with the
> contacts of 12 volt DC relay driven by a microcontroller.
>
> The relay contacts arc and I thought a snubber will reduce the arcing.
> I checked various sites and ended up lots of calculations for which I
> have no proper data.
>
> Is there a ball park value I can use for the capacitor and the
> resistor?

I would pick a resistor that passed a peak current that is
about the same as the highest peak current the contactor
draws. Unfortunately, that number may be hard to come by.
But you might estimate it as several (say, 3) times larger
than the rated coil current. So if the contactor coil
current is rated to be about 0.1 amp, I would pick a
resistor that is the peak line voltage divided by 0.3 amps
or 240*1.414/0.3=1.1k, so lets say, 1k ohms. That way, if
the contact happens to close at peak voltage, the contact
won't have to deal with a resistor inrush current much
greater than what the relay will draw within a half cycle.

Most RC arc suppressors you can buy have lower resistances
in them, most from 220 to 47 ohms, but most are intended for
loads heavier than a relay coil.

Ideally, the capacitor value is based on the inductance of
the coil and its energy storage (proportional to the peak
current squared), but too large a capacitance is safe (will
absorb the inductive energy at a safe voltage peak), as long
as it doesn't overheat the resistor. So lets say you use a
1 watt resistor (more the peak voltage rating or 300 volts
than anything else) and pick a capacitor that will dump a
half watt into it. by W=I*I*R, 0.5 watt=I*I*1k, so I=22
milliamps. If that current is limited by the capacitor
across 240 volts, that implies a capacitive reactance, by
Xc=1/(2*pi*f*C) and Xc=240/0.022=10700 so C=0.25 uF. I
would probably go with a 0.22 uF, 600 or 1000 VDC capacitor
in a pinch, but the right kind is one rated X1, for across a
240 volt AC line.
This sort of thing:
http://www.panasonic.com/industrial/com ... 00ce30.pdf

I hope that helps you (and I didn't hit a wrong calculator key).

--
Regards,

John Popelish


17 Mar 2008, 17:08
Post Re: Snubber
ClueLess wrote:

> Hi all
>
> I want to start a motor remotely.
>
> The contactor coil is rated 240 volts and I am driving it with the
> contacts of 12 volt DC relay driven by a microcontroller.
>
> The relay contacts arc and I thought a snubber will reduce the arcing.
> I checked various sites and ended up lots of calculations for which I
> have no proper data.
>
> Is there a ball park value I can use for the capacitor and the
> resistor?
>
> Thanks in advance for your time and attention
>
> ClueLess
>
>

100F in series with a .1 uf 600v cap maybe?
You could use just the cap across the terminals
how ever, if the cap becomes fully charged and then
you induct even more, it could short the cap.
Using the R in series helps with a slower charge.


http://webpages.charter.net/jamie_5"


17 Mar 2008, 17:08
Post Re: Snubber
On Mar 9, 7:15=A0am, ClueLess <cluel...@wilderness.org.invalid> wrote:

> I want to start a motor remotely.
>
> The contactor coil is rated 240 volts and I am driving it with the
> contacts of 12 volt DC relay driven by a microcontroller.
>
> The relay contacts arc

Yep, there is switch bounce and the motor has stray inductance.
Your easiest option is a surge suppressor type device,
like MOV or ZNR varistors. In the old days, a resistor-capacitor
pair with some size adjustment to the inductance was recommended,
but that's too much like engineering...


17 Mar 2008, 17:08
Post Re: Snubber
Paul E. Schoen wrote:

> I use self-contained snubbers that are 100 ohms in series with 0.1 uF for
> contactor coils, and that seems to be a good combination for most sizes.
>
> At 240 VAC 60 Hz, the resistor will dissipate about 8.8 mW with 9.4 mA.
>
> I did a simulation with LTspice for a 240 VAC coil with 5H inductance
> (which draws 130 mA or 31 VA sealed-in). This is probably about right for a
> good-sized contactor rated at 40 amps or so.
>
> Under best conditions, if you apply the voltage at a waveform peak, the
> inrush current is 180 mA peak, which is the same as continuous waveform. In
> actual proctice, however, the peak inrush will be much higher (perhaps
> 5-10x) because the inductance is much lower when the clapper is separated
> from the electromagnet. If the circuit is opened near the zero current
> point, there is just some ringing but no voltage overshoot.
>
> Now look at worst case conditions. If you apply voltage at the waveform
> zero crossing, you get a peak current of 355 mA, and a "DC offset" of coil
> current that persists for several cycles.
(snip)

I can only guess that all these currents are coil currents.
What is the worst case snubber current at turn on? It
should exceed 3 amperes, right when the contacts are
bouncing closed. For such a light load, I think a 100 ohm
snubber resistor is well below the optimum compromise for
contact life.

--
Regards,

John Popelish


17 Mar 2008, 17:09
Post Re: Snubber
"John Popelish" <jpopelish@rica.net> wrote in message
news:3JKdnd4oUpl3VUnanZ2dnUVZ_hadnZ2d@comcast.com...
> Paul E. Schoen wrote:
>
>> I use self-contained snubbers that are 100 ohms in series with 0.1 uF
>> for
>> contactor coils, and that seems to be a good combination for most sizes.
>>
>> At 240 VAC 60 Hz, the resistor will dissipate about 8.8 mW with 9.4 mA.
>>
>> I did a simulation with LTspice for a 240 VAC coil with 5H inductance
>> (which draws 130 mA or 31 VA sealed-in). This is probably about right
>> for a good-sized contactor rated at 40 amps or so.
>>
>> Under best conditions, if you apply the voltage at a waveform peak, the
>> inrush current is 180 mA peak, which is the same as continuous waveform.
>> In actual proctice, however, the peak inrush will be much higher
>> (perhaps 5-10x) because the inductance is much lower when the clapper is
>> separated from the electromagnet. If the circuit is opened near the zero
>> current point, there is just some ringing but no voltage overshoot.
>>
>> Now look at worst case conditions. If you apply voltage at the waveform
>> zero crossing, you get a peak current of 355 mA, and a "DC offset" of
>> coil current that persists for several cycles.
> (snip)
>
> I can only guess that all these currents are coil currents. What is the
> worst case snubber current at turn on? It should exceed 3 amperes, right
> when the contacts are bouncing closed. For such a light load, I think a
> 100 ohm snubber resistor is well below the optimum compromise for contact
> life.

I tried again with a 0.47 uF capacitor and a 270 ohm resistor, and the
transients are now limited to 600 volts peak. The snubber power is only
about 1/2 watt (44 mA), and peak current will be limited to 360/270 = 1.3
amps. The worst case current for the contacts will be when they first close
into the initial inductance of the coil, which could result in 3-4 amps of
inrush current. And the most damage may happen as the contacts bounce on
closure. But the snubber will greatly reduce the arcing upon opening, which
is really metallic ions transferring from one contact to the other, or onto
the surrounding insulation, causing the familiar metallic deposits that are
seen in relays with pitted contacts.

There are some trade-offs with puttong the snubber across the coil (as I
normally do), or across the relay contacts. In this case, when energized,
the snubber draws an additional 44 mA, but the total load on the supply is
only 85 mA, while the relay coil itself draws 129 mA. So the snubber
actually helps the power factor and reduces load on the supply. Placed
across the switch, it will apply a constant leakage current to the
contactor coil, which could be enough to cause humming, and an unwanted
potential when it is supposed to be deenergized. But in other cases, such
as for SCRs, it is customary to put the snubber across them.

A better solution might be to use a solid state relay (triac or SCR) which
can be driven directly from the microcontroller. You can get them for
inductive loads, but even the zero voltage turn-on types will not cause too
much problem for a motor load. Of course, a soft-start full featured PWM
controller is best, but probably overkill.

Paul


17 Mar 2008, 17:09
Post Re: Snubber
"whit3rd" <whit3rd@gmail.com> wrote in message
news:8aab4ecf-1c36-4dc9-81c9-edafacdb12c2@n75g2000hsh.googlegroups.com...
> On Mar 9, 7:15 am, ClueLess <cluel...@wilderness.org.invalid> wrote:

>> I want to start a motor remotely.
>>
>> The contactor coil is rated 240 volts and I am driving it with the
>> contacts of 12 volt DC relay driven by a microcontroller.
>>
>> The relay contacts arc

> Yep, there is switch bounce and the motor has stray inductance.
> Your easiest option is a surge suppressor type device,
> like MOV or ZNR varistors. In the old days, a resistor-capacitor
> pair with some size adjustment to the inductance was recommended,
> but that's too much like engineering...

The problem with MOVs and ZNR varistors is that they have a limited
lifetime, and deteriorate with every surge they absorb. As they begin to
fail, they get more leaky, and conduct at lower voltages, until they
overheat and explode. You must put a fuse in series with them, and when the
fuse blows, you no longer have protection. There are some zener type TVS
protectors that do not deteriorate, but RC snubbers are still the best for
controlling transients. The ideal solution, however, is to eliminate the
transients by using solid state controls such as triacs and SCRs.

Paul


17 Mar 2008, 17:09
Post Re: Snubber
On Mar 9, 11:37=A0pm, "Paul E. Schoen" <pst...@smart.net> wrote:
> "whit3rd" <whit...@gmail.com> wrote in message

> > Your easiest option is a surge suppressor type device,
> > like MOV or ZNR varistors.

> The problem with MOVs and ZNR varistors is that they have a limited
> lifetime, and deteriorate with every surge they absorb.

This is true, but the surges one usually associates with varistors
are lightning-strike kinds of events, much higher currents than
a little spark on a motor-start relay.

In this duty, I'd expect a long useful component life.

There is some confusion, though, on the snubber function: this
calls for a snubber or varistor across the MOTOR leads, not
across the relay contacts (which would result in running the
motor if it fails short) nor across the winding (winding current
wasn't arcing, as I read the situation). The varistor, if it fails
short circuit, pops the circuit breaker just like a shorted motor
would.


17 Mar 2008, 17:09
Post Re: Snubber
"whit3rd" <whit3rd@gmail.com> wrote in message
news:0b26693a-c9a7-4232-9272-4802b52ff093@s50g2000hsb.googlegroups.com...
On Mar 9, 11:37 pm, "Paul E. Schoen" <pst...@smart.net> wrote:
> "whit3rd" <whit...@gmail.com> wrote in message

> > Your easiest option is a surge suppressor type device,
> > like MOV or ZNR varistors.

> The problem with MOVs and ZNR varistors is that they have a limited
> lifetime, and deteriorate with every surge they absorb.

This is true, but the surges one usually associates with varistors
are lightning-strike kinds of events, much higher currents than
a little spark on a motor-start relay.

In this duty, I'd expect a long useful component life.

There is some confusion, though, on the snubber function: this
calls for a snubber or varistor across the MOTOR leads, not
across the relay contacts (which would result in running the
motor if it fails short) nor across the winding (winding current
wasn't arcing, as I read the situation). The varistor, if it fails
short circuit, pops the circuit breaker just like a shorted motor
would.

>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>

It is not totally clear whether the arcing was on the contacts of the small
relay being driven by the microcontroller, or the larger contactor that
controlled the motor. But I think it was the small relay, and for that I
think the snubber across the contactor coil is best. A motor is a reactive
load as well as a regenerative load, so it will produce a high voltage
spike if the AC current is interrupted at a peak, but it may also tend to
act as a generator and try to inject voltage back into the supply. A
snubber would function somewhat as a dynamic brake.

MOVs should be protected by a fuse much smaller than the fuse or circuit
breaker of the mains supply, as they usually have fairly small leads, and
if allowed to absorb the full short circuit instantaneous trip current of a
mains breaker (say 150 amps), at full voltage (240 VAC), that is 36 kW,
which can do a lot of damage even in a few milliseconds. The MOV protector
should be something like a 1 amp fast blow fuse.

If the motor will be turned on and off only occasionally, there may never
be a problem, but for repetitive use, deterioration of the MOV is
inevitable, and it is not that difficult or expensive to use a proper
snubber (or better yet, solid state phase control).

Paul


17 Mar 2008, 17:09
Post Re: Snubber
On Sun, 09 Mar 2008 19:45:05 +0530, ClueLess
<clueless@wilderness.org.invalid> wrote:

>Is there a ball park value I can use for the capacitor and the
>resistor?

I am really overwhelmed at the many responses my question evoked.
Thanks to all of you for giving me some leads and I am looking forward
to the weekend on my workbench toying with what I have learnt.

Thanks again to all of you

ClueLess





































--
Posted via a free Usenet account from http://www.teranews.com


17 Mar 2008, 17:09
Post Re: Snubber
On Tue, 11 Mar 2008 02:10:10 -0400, "Paul E. Schoen"
<pstech@smart.net> wrote:

>It is not totally clear whether the arcing was on the contacts of the small
>relay being driven by the microcontroller, or the larger contactor that
>controlled the motor. But I think it was the small relay, and for that I
>think the snubber across the contactor coil is best.

Yes, arcing is on the small 12 volt relay. This relay is the totally
enclosed variety and for testing I cut away the outer casing so the
contacts are visible. There is arcing when driving the contactor coil
and I wanted suppress that.

Thanks for your interest and help

ClueLess


























--
Posted via a free Usenet account from http://www.teranews.com


17 Mar 2008, 17:09
Display posts from previous:  Sort by  
Forum locked This topic is locked, you cannot edit posts or make further replies.  [ 11 posts ] 


Who is online

Users browsing this forum: Google [Bot] and 2 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB © phpBB Group, phpBB SEO.
Designed by Vjacheslav Trushkin for Free Forums/DivisionCore.